Communication with ML-1000

pravinshinde

Member
Join Date
Feb 2009
Location
pune,India
Posts
57
Hi all,

I have one Ml-1000 I want to communicate with this PLC through serial port.

I do not know node address of this PLC,as someone has assigned node address to this PLC.

Due to this I am not able to get auto configuration successful msg.

Any solution for this ?
 
but i do not know previous node address...it will not give autoconfiguration successful msg
Ml 1000 has round type female connector
 
Last edited:
Make sure you set the device to be a SLC-CH0/Micro/PanelView. In serial, the node address does not matter, I always use 0. Make sure you have the right comm-port selected.
 
I have total 15 PLC's.I am able to communicate with 14 PLC's.If I do not mention correct node address my laptop is not communicate with PLC.
What I observed is, I need to set correct node address.
As you suggest me I have took care of device selection and copm port.
 
RS-232 DF1 Devices

Then leave the "Station Address" in RSLinx at "0".

Depending on the ML1000 you have it's port can be configured for DH485.

Do you have it's offline file. If so take a look at the port configuration settings. Or post the file here.
 
Actually I have tried with different node address from 0-15,but it gave me no result.

I have attached old back up file but I am sure that PLC node address is other than 11.

Image.jpg
 
With the port on your ML1000 configured for DF1 Half Duplex Slave you will have to use
the "DF1 Polling Master Driver" in RSLinx.

Or if you have a series "D" or higher controller see pdf below for "Automatic Protocol Switching" feature. And use the DH485 driver ( will need a real serial port or a 1747-UIC for this.
 
Last edited:

Similar Topics

Hi, I'm wondering if anyone knows whether it is possible to communicate between a Micro820 w/ a 2080-SERIALISOL and a PowerMonitor1000 via Modbus...
Replies
2
Views
559
Hi Guy, some times i receive this message in my PV1000: 637 Communication Driver has FAULTED -contact technical support. after there is no...
Replies
11
Views
3,845
Hi all, after much aggravation trying to get my SLC5/04 to talk half duplex to RSlogix so l then would be able to communicate with both RSlogix...
Replies
0
Views
2,239
i am trying to communicate to my pv1000 by the rs232 port using rs linx which is not detecting the pv1000. please to assist me with this problem...
Replies
14
Views
2,829
Hello, I am trying to use micrologix 1400 Ver.A as adapter and a Productivity P1-540 as scanner, only Ethernet/IP is supported by ML1400 Ver.A...
Replies
2
Views
1,853
Back
Top Bottom