Can I upgrade the 1100 from an "A" to a "B"? On Rockwell Web site, I see a series B upgrade, but I think that just brings an 1100 already a "B" to a higher series.

Thanks
George
 
In the Rockwell Automation world, a Series change is either a major hardware change, a major functionality change, or both.

In the case of the MicroLogix 1100 controller, it's a firmware functionality change only. The original Series A hardware can be upgraded to run the Series B firmware.

MicroLogix family controller firmware upgrades don't require a TechConnect contract; just download and install the firmware you see on the website.
 
I just tried to upgrade. This is where I got stuck ( see attachment) my Processor is 1763-L16BWA. It won't go past this point.
Thanks
George

Firmware upgrade.png
 
Last edited:
Mickey,

Thanks, That helped update the firmware. I was hoping it would allow me to send email. But the SNMP is still greyed out on the Channel setup for email. Am I still missing something?

Thanks
George
 
SNMP is Simple Network Management Protocol, used by IT service monitoring software. I can't enable it on my MicroLogix 1100 either.

SMTP is Simple Mail Transport Protocol, which is the e-mail sending client. This should be selectable.

Remember that you need to change the Controller Type to MicroLogix 1100 Series B, and therefore you need an appropriate version of RSLogix 500.
 
Ken,
That is what I was looking for. SMTP, for email. I guess upgrading the firmware didn't enable this.
Thanks
George
 
Gosh, it certainly should have. MicroLogix 1100 Series B firmware has no hardware-dependent features, which is why you can install it on Series A controllers.

What version of RSLogix 500 are you running ? Are you sure you've changed the Controller Type to a MicroLogix 1100 Series B ?
 
I just went to show that I don't have that option by taking a screen print and there it was. Thanks for the help. Now I can see if I can send an email.

Thanks
George
 

Similar Topics

I using a HSC:0 with no problem with a encoder, but I am not able to add the second channel in order to use the HSC:1. float memory is at F8:29...
Replies
2
Views
968
Hi, I have a project where I'm replacing a faulty Mitsubishi FX3s plc with a Micrologix 1100. The FX3s was using a GS2107-WTBD HMI panel. The HMI...
Replies
2
Views
1,113
I have a few previous PLCs that are installed which say they are Micrologix 1100 Series A PLCs but does this mean they are 1763-L16AWA or...
Replies
1
Views
1,465
Dear Forum Members, I'm new to the world of plcs and their respective programming. So I apologize for my ignorance, and thank you in advance for...
Replies
2
Views
1,595
I am connecting via the Mini Din to Serial to USB, and cannot get the Mac Address to come up in BootPHP. I have previously tried with Ethernet and...
Replies
10
Views
2,824
Back
Top Bottom