will 2094-ac16-am03-s with 1 module down work?

mike_dr

Member
Join Date
Sep 2011
Location
Mla
Posts
215
the L43 logix controller is connected to 2094-ac16-am03-s IAM and,two 2094-AM02 and 2094-AM03 but one AM02 module does not show any transition phase at all but has logic power (dot at led) on. I didn't define the unresponsive (AM02) module in rslogix 5000 and just powered up the 3 servos (using MSO) except the unresponsive one and got another problem at AM03 which is motordata: invalid attribute value. is it because of the one (possibly) broken module or this is an another isolated problem. the AM02 module's Rx Tx port is not connected anymore. Highly Appreciate veteran's help because I am just a newbie.
 
Last edited:
There is also another error which I think is possibly related to the motordata error of AM03.The IAM module comm status is blinking red then yellow(?) and the drive status is red. I have checked about baud rates, auto detect communication rate. the motor feedback and the cable to the servo of the unresponsive AM04 module is unplugged so that it would seem to be non-existent. Is that wrong?

Do I have to use MSF then MSO to update motordata which I did not change from the start? Although I just copied everything from the recent program in the controller, everything is the same except I removed the AM02 module and deleted any instruction related to the axis. Thanks again to the response
 
turns out LIM wasnt enabling drives due to faulted kinetix module so the solution to enable the working ones was to short the contactor enable pins of AM16-m03. ~~
 

Similar Topics

Let me start with, I know nothing about Kinetix 6000 or Sercos. We have a machine that we've bought that we're trying to refurbish to sell on -...
Replies
2
Views
3,190
Hi folks: Has anyone replaced a 2094-BM01-S with a 2094-BM02-S ?. I know they are different , but I have a BM02 spare and want to use it. Is this...
Replies
1
Views
1,394
Hey all. Just a few quick question, before I spend hours of reading the manual myself. I'm at a site, where the software knowledge is limited...
Replies
4
Views
2,361
Good Afternoon , I have a strange situation . We have a machine that has several Kinetix Servo drives and motors on. We had a maintenance...
Replies
1
Views
2,983
I have the new servos up and communicating. Will the tag names in the motion group be the same or are there new tag names associated with the new...
Replies
0
Views
1,949
Back
Top Bottom