if i want high sensitivity what is the best solution RTd or thermistors?.
ok, now i need to know the suitable shape to be connected to plc.
mado said:fatek plc has analog input
. . .
probe that can be inserted in industrial environment and can be connected to plc via cable.
fatek plc has analog input ,I mean with suitable shape something like probe that can be inserted in industrial environment and can be connected to plc via cable.
I need thermistor because it's high sensitivity . i need degree of tens like 0.3 which i won't find it in RTD, so i asked your practical experience in this type of measurements . i know many types of sensors available but which one ?. and don't worry about plc i will take care of it.
Is it possible he meant thermocouple? EDIT: No, he has a specific type, either way he will need a transmitter.
To mado:
If you have 24vdc, get an RTD and a suitable transmitter from automationdirect.com
They are cheap, accurate, and I use them in Room Temperature (about 0F to 105F) freezers (-30F to 180F), and gas HVAC heater ducts (30 to 300), and hot water applications (190F).
Very easy to install with the DC Micro connectors:
http://www.automationdirect.com/adc/Shopping/Catalog/Sensors_-z-_Encoders/Temperature_Sensors_-a-_Thermometers/RTD_(PT100)_Sensors/Probes_(with_M12_Cable_Connection)