I'm in need of some insight regarding the memory structure of a Modicon PLC.

In the program %M130 is being SET and RESET in ladder logic but elsewhere in the program %MW130 is also referred to in an "OPERATE" instruction.

How is the memory organised? Does setting %M130 set all bits in %MW130 to 1?

Please see attached code.

Thanks in advance,

Nick
 
%M130 is a bit, %MW130 is a word.
They are not related. The format for the bits in a word are for example %MW100:X0 as being the least significant bit, and %MW130:X15 is most significant.

The operate instructions in your case are table instructions.
To describe the following:

%MW130:10:=%MW120:10

The contents of a table 10 words long, starting at %MW120 is transferred or moved to a table 10 words long starting at %MW130.

contents of %MW120 to %MW130,
contents of %MW121 to %MW131,
etc.


Deciphering the following instruction:

%MW110:10:=0

Value of 0 transferred or moved to a table, 10 words long, starting at %MW110, meaning %MW110 to %MW119 are loaded with the value 0

One of my favourite all time machines, the TSX57.
If you need any more help, just let me know.
 
Liam, Thanks very much for your reply, it was most helpful. We are converting an old Modicon system to Siemens Step7. We'll continue to try and understand the oroginal code.

Nick
 

Similar Topics

I have a Modicon TSX57 and am using PL7 Pro. I can not connect to the PLC through citect, I receive this error message..."Not possible to...
Replies
1
Views
4,101
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
244
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
Replies
0
Views
82
Hi, Seeking consultation on an implementation matter, and have a question about Modicon Compact 984 communication through RS485: Three Modicon...
Replies
4
Views
199
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
128
Back
Top Bottom