I feel like a complete dunce asking this question, but I can't find any information pertaining to it in the instruction manuals or online.

I'm passing a DINT parameter via JSR to my SBR and getting:
Error: Rung 0: Missing output instruction. because I have no idea what to use as my output instruction. In example code and in the instruction manual there is an OTE following the SBR, but I just don't get it. What is the point of an output following the SBR? Can't I just pass my DINT in to the routine and be done with it? I have no reason to output anything on the first rung, no logic to support it.

I can MOV the DINT parameter into itself to satisfy the error but that just seems silly...I would appreciate some guidance on this. I'm super frustrated.
 
Just put a dummy coil on the SBR rung, or put the SBR on the first rung of the code inside the routine.

The SBR requires that an output instruction exist on the rung along with it, which is another reason to omit it entirely unless passing parameters in which case, you have to follow its rule which is probably a legacy of older controllers.
 
Originally posted by OkiePC:

The SBR requires that an output instruction exist on the rung along with it, which is another reason to omit it entirely unless passing parameters in which case, you have to follow its rule which is probably a legacy of older controllers.

The SBR is an input instruction. Logix won't let you accept a rung with just a contact on it either.

If you are passing a parameter into a subroutine you will presumably have at least one output instruction esulting from processing the data you are passing. AB needed to make the thing something and it seems pretty reasonable (IMHO) that it be an input instruction.

Keith
 
The SBR is an input instruction. Logix won't let you accept a rung with just a contact on it either.

If you are passing a parameter into a subroutine you will presumably have at least one output instruction esulting from processing the data you are passing. AB needed to make the thing something and it seems pretty reasonable (IMHO) that it be an input instruction.

Keith

Yes, it makes sense to me just the way it is.

But, like having multiple OTE in series, it is probably something that could have been allowed (SBR by itself) in RSLogix5000, except that we really don't want or need another exception to the rules of behavior among the A/B product families' instructions which are named the same.
 

Similar Topics

Hello, I am stuck and need advice on using SBR in ST using RSLogix 5000. I am very new to ST, mainly have used If and End_If. I have tried to read...
Replies
1
Views
1,369
Hi, I have been tasked to test JSR/SBR instructions using parameters in RSLogix 5000. I found a video that was extremely helpful using 1...
Replies
12
Views
2,500
Hello Gurus, I am working on the elevator exercise of LogixPro and my output on the subroutine is being energized without its flag being called...
Replies
4
Views
2,166
Hello All, I'm relatively new to PLC programming, Ladder Logic, Structured Text, SFC, etc. I have roots in Java, C#, PHP and other languages. I...
Replies
9
Views
4,835
I am wanting to use a subroutine to do data calculations to separate and combine 32bit and 16 bit words. I am doing this to move data to and from...
Replies
10
Views
3,664
Back
Top Bottom