Micro 1400 HSC configuration

Join Date
Aug 2011
Location
Darnum
Posts
14
Hello,
I am trying to configure a 1400 for two quadrature encoders. I've got one hsc working ok using inputs 2 and 3, but does anyone know how to configure the second one to look at inputs 4 and 5?
 
Can you give us the catalog number of your ML1400.

Do you have a common wire onto Com1, as it is the common for inputs 4 and 5, just as Com0, is the common for inputs 0, 1, 2, 3.

Also HSC is I believe accessed via the Function file in your project tree.
 
Last edited:
Do you mean hsc:1? when I configure this it actually stops hsc:0 from working.
I was thinking that maybe I need to tell it which inputs to use.

yes, hsc:1 is function file .1 for the HSC.

The answers you seek are in the manual.


http://samplecode.rockwellautomation.com/idc/groups/literature/documents/rm/1766-rm001_-en-p.pdf

The I/O assigment is fixed, you do not have to allocate them.

All MicroLogix 1400, except the 1766-L32AWA and 1766_L32AWAA, have six
100kHz high-speed counters. There are three main high-speed counters (counter 0,
1, 2) and three sub high speed counters (counter 3, 4, 5). Each main high-speed
counter has four dedicated inputs and each sub high-speed counter has two
dedicated inputs. HSC0 utilizes inputs 0…3, HSC1 utilizes inputs 4…7, HSC2
utilizes inputs 8…11, HSC3 utilizes inputs 2 and 3, HSC4 utilizes inputs 6 and 7
and HSC5 utilizes inputs 10 and 11. In some cases, a sub counter will be disabled

by master counter mode. See the section HSC Mode (MOD) on page 94.
 

Similar Topics

Hi! Last few I've been trying to send message from MicroLogix 1400 to Micro 850. Unfortunately every time I failed :banghead:. Did someone tried...
Replies
6
Views
3,177
Hello, There was a mix up in information on some redeployed equipment and two of the micro 1400's that came in were hooked to 120v when they...
Replies
9
Views
1,947
I am trying to exchange data (N registers) to and from a Control Logix PLC. I am programming the messages in the Control Logix program, to...
Replies
7
Views
2,147
Does the 1100 only have 1 high speed counter, but it can have multiple inputs? And so then the 1400 has 6 HSC and you have a choice of multiple...
Replies
1
Views
1,714
Error: "Program in processor has changed causing offline state. Do you want to upload?" RSLogix500 V8.10 Micrologix 1400 Customer wants to add...
Replies
8
Views
2,263
Back
Top Bottom