Can I do this? I would like to have the 24vdc output on the vfd (abb ach550) power a 24vdc coil, then the start stop can latch using one of the contacts (using push buttons with contact blocks vs. a switch). I contacted ABB and the 24vdc provides up to 250mA. The omron coil draws about 62mA, so it looks like it should work.
thanks
 
I'm sure opinions will differ on this. I have used the internal supply before without issues. Never exceed 80% of the supply rating. Only thing that comes to mind for me is no mention of an E-stop. Not sure of the application so that would dictate saftey requirments.
 
For this particular application no E-stop is necassary, just a stop button and a start button.
 
Mat,

Yes, your method will work, but most VFDs have some dry-contact relay outputs (programmable in many cases) that can be used with any external control-voltage supply to latch in a Start-Stop circuit.
 
I was looking at OMRON ly4-dc24, it has power consumption as 1.5 watt. I could have calc'd it wrong but I think it comes out to 62.5mA
 
I haven't used the dry contacts before, would i just wire the NO start button in parallel with the dry contact?
 
I'm not familiar with your particular model, but many VFDs have a parameter you can set to specify how the the drive deals with start/stop signals. You may be able to have the drive seal in a momentary start command without having to use one of the outputs.
 
Yes, Steve is right. I read this thread but it didn't dawn on me what he was doing with the relay until Mr. Bailey posted.

Get the manual for the drive and search for "3 wire" mode. This lets you wire up a normally open momentary button to the start input and a normally closed button to the stop input. The drive will start when the stop input is on and the start input is on. The drive will continue to run after the start input is off as long as the stop input stays on.

No relay required.

I am pretty sure ABB will call that style of wiring 3 wire mode.


EDIT2: Uhhh, maybe not. That manual shows no control wiring, rather its an HVAC drive with a remote keypad module...

EDIT1: ACH550-UH User’s Manual
 
Last edited:
Yes, except the ACH550 User Manual, Page 1-319, shows the drive Terminal Block numbers for the N.O. dry contact of the Relay 2 to be 22 and 24 (instead of TB14 and TB16 as you have them labeled). Apparently you have a different control board than the one shown in the User Manual.
 
No it will not work to many connections.
The light should go direct to ground on one side and on other side direct to relay from relay to 24 volt.
Now the light will short the start button.
 
Shooter, you are correct. I did not even look at the light, instead checking the new relay seal-in circuit. But as it is, the light resistance will always be parallel to the start button, which could cause a false start command. If it is wired to the Relay TB16 and to -24 VDC, then it should work.
 

Similar Topics

Sorry, this is not PLC related. Is it possible to use miniature DIN rail mounted single pole AC circuit breaker (rated 480VAC) as overcurrent...
Replies
8
Views
7,690
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
49
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
111
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
219
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
56
Back
Top Bottom