ET200L problem

eams2010

Member
Join Date
May 2009
Location
Alex
Posts
26
Hi All,
I have an ET200L module with part no. 133-1BL01-0XB0. I'm trying to connect it to a CPU317-2 PN/DP through profibus. The Problem that I can not find this part no in the hardware, so I can not add it to the hardware configuration. I searched in the internet and found the GSD file for this module, I installed it but still can not find it in the hardware.
I'm using V5.5.
regards
 
You can find it in the HW Catalog:
"6ES7 133-1BL0*-0XB0
Digital I/O 16DI x 24 VDC; 16DO x 24 VDC, 0.5 A, non-expandable, send capability for direct communication"
 
I dont understand what goes wrong for you.
Have you tried to drag-and-drop the abovementioned module from the catalog to the Profibus network ?
What error message do you get when you try ?
 
Yes I draged and dropped the module to the profibus network. I adjusted the address to be the same as the hardware address. saved and compiled, then downloded the hardware configuration to the PLC. What I got is SF, BF, and the error in the diagonistic buffer is the found module is not matched with the insterted one.
 
What I got is SF, BF, and the error in the diagonistic buffer is the found module is not matched with the insterted one.
This is Siemens lingo for many possible error types. It can be that the DP slave is not accessible at all.
 
C:\ET200L.JPEG


Attached the Error I got
 
It is working now
I do not kn ow what was the problem
I did the same as I'm doing every time and it worked
Thank you
 

Similar Topics

How do I do This???? We are into PLC training and intend to show CPU Redundancy on Siemens S7 412 2DP cpu's. I have following Hardware (a)...
Replies
4
Views
8,790
Does anyone have a source for old Siemens ET200L Profibus Modules? I have several that are bad and need to be replaced. I don't want to replace...
Replies
12
Views
5,591
Hi I have an ET200L with an SC expansion 2 analogue input cards on slots F and G. The weird thing is, that Physically, the current inputs...
Replies
2
Views
2,103
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
61
Hi everyone, I'm trying to simulate any program in control expert and see a register in Modscan32 or any software to do that (Like ModbusPoll). I...
Replies
0
Views
62
Back
Top Bottom