pt100 signal goes open in mirologix 1400

md.abdullah

Member
Join Date
Sep 2011
Location
motihari
Posts
168
hello friends
i have installed a system for the wax feed
in which i have to control the temperature for this purpose i used pt00 for temperature ranges 16 to 204 degree c
i have used a module 1762-ir4
but problem is signal from the pt100 does come to module also come to the plc but after some time it shows 8500 if i changed to downscale then it shows -2000 means it goes open the signal i have used ssr for the heating purpose
i have used scale 0-4095 and 16-204 temperature
can any one tell me what is going there ?
 
It is very likely that the conductors for the RTD sensor are becoming an open circuit and the module is correctly indicating that status.

From page 1-7 of the User Manual (Publication 1762-UM003):

Each time the module reads an input channel, it tests the data for a
fault (over- or under-range, short-circuit, or open-circuit condition). If
it detects a fault, the module sets a unique bit in the channel status
word.

Do any of the status bits in the Input data table indicate an open-circuit ? These are illustrated on page 3-3 of that same User Manual.

How is the condition repaired: does the system cool down, or do you cycle power, or something else ?
 

Similar Topics

Hi guys I was wondering if it is possible to split a pt100 probe signal , I have a pt100 going to a controller but I would like to piggy back off...
Replies
10
Views
8,703
How do major PLC manufacturers (Allen Bradley, GE, Siemens, etc.) get the temperature sensing signal for a PT100 or PT1000 into a PLC? Is there...
Replies
6
Views
6,154
Have you seen a PT100 sensor reading going slowly up, even after heating power turned off ?! and it keeps rising for several minutes ... It looks...
Replies
11
Views
4,473
Im having a 3wire pt100 connected to a temperature transmiter. Im reading the current in the loop and I have 22mA, so is overrange. What could...
Replies
6
Views
1,678
Hi. Almost every time when working with PT100 probes the customers ask me "have the probes been calibrated?" The reason for the customers to ask...
Replies
18
Views
5,055