Hi
Sorry for the long explaination
I am commisioning a new install with these PID control blocks which are supposedly auto tuning.
The process is cooling, and is a 1 shot process via a heat exchanger, with a modulating valve controlling the cooling medium.
I have FB58 within OB35 on a 1 second cycle time and i have coded the gains to be negative.
I need to cool the product from 85 to 35C.
With P only I get a swing of about +/- 10C over a time period of about a minute. I used the ziegler nicholls idea and used 20 seconds for the I term and 8 seconds for the D term ... useless
So, I tried to use the autotuning.... Now the options are to use a step change or to try and tune around the setpoint.
I enabled the process and enabled auto tune (step change) and altered the setpoint by 30 Degres but the tuning block just sat their scanning for over 10 minutes eithout moving from step 0.
I gave up and tried the around the setpoint idea but this also didnt do much apart from give an output of 40% and sit like that for about 10 minutes.
So
A -- Am i to impatient... does the tuning take ages. Based on instrumentation i have used in the past this would take typically 30s-1 minute.
B -- Any better stragy is more than welcome. i am thinking of trying a PI control tomorrow
C Is the self tuning of FB58 aactually amy good
Cheers
Sorry for the long explaination
I am commisioning a new install with these PID control blocks which are supposedly auto tuning.
The process is cooling, and is a 1 shot process via a heat exchanger, with a modulating valve controlling the cooling medium.
I have FB58 within OB35 on a 1 second cycle time and i have coded the gains to be negative.
I need to cool the product from 85 to 35C.
With P only I get a swing of about +/- 10C over a time period of about a minute. I used the ziegler nicholls idea and used 20 seconds for the I term and 8 seconds for the D term ... useless
So, I tried to use the autotuning.... Now the options are to use a step change or to try and tune around the setpoint.
I enabled the process and enabled auto tune (step change) and altered the setpoint by 30 Degres but the tuning block just sat their scanning for over 10 minutes eithout moving from step 0.
I gave up and tried the around the setpoint idea but this also didnt do much apart from give an output of 40% and sit like that for about 10 minutes.
So
A -- Am i to impatient... does the tuning take ages. Based on instrumentation i have used in the past this would take typically 30s-1 minute.
B -- Any better stragy is more than welcome. i am thinking of trying a PI control tomorrow
C Is the self tuning of FB58 aactually amy good
Cheers