i have a pt 100 temprature sensor it have three wire 2 white and 1 red ,,i asked to alen Bradly support people about wiring they said me to buy a transmitter for my RTD which can convert its resistance in voltage or current ..

now I have a ml1100 which have two analog input port and one common port for both of them .....

its input value is given in 0 to 10 volt in the manual ...

when i went to market i asked for RTD transmitter he told me about 4-20 mA 0-20 mA 0-10 volt type of transmitter

suggest me which type i have to buy and why i have to buy that particular type :rolleyes:

I HAVE CAT NO. OF PLC 1763 L16BBB
 
The RTD transmitter itself is only part of the cost.

The 0-10V output of the RTD represents some temperature range, say, 0-100°C.

If the factory default range is not correct for what you need, then the range needs to be changed, typically with PC software and a modem/cable device. Depending on brand and model, that PC software and modem/cable can range from free to $5,000 USD.

If this is a one time deal, you might consider buying an RTD transmitter whose software/modem is free or from a vendor who will range it for you, so that you do not have to invest in software and a modem for a one-time range operation.

Good Practice is to put an adhesive label on the RTD transmitter with its range.
 

Similar Topics

Hi every body i m doing electrical engg (specialization in Electronics) i wana do PLC based project i need help to chose final year project plz...
Replies
3
Views
2,910
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
264
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
Replies
4
Views
166
Hi ,when i check the 4-20 ma output from flowtransmitter with multimeter ,it can shows 4 ma , but when i check with process meter it only shows...
Replies
1
Views
160
How fail safe mode in level transmitter works? customer requesting for fail safe mode when the transmitter got any issue or power loss on the...