Ml 1500

osamamalhy

Member
Join Date
Jan 2006
Location
alex
Posts
89
Greetings
i have ML1500 LRP (C), i want to use port number(1) as Modbus master , what i need is the D connector configuration , also the end resistance connection in both sides
 
Hi Osama,

The Channel 1 port on a MicroLogix 1500 "1764-LRP" controller is a "DTE" type RS-232 port.

This means that the pinout conforms to the Data Terminal Equipment (DTE) standard for RS-232 on this type of connector: http://www.db9-pinout.com/.

This is identical to the serial port on an ordinary laptop computer. It's also described in the MicroLogix 1500 User Manual on page 4-6.

Because RS-232 is only a point-to-point connection, there is no termination resistor used. If there is an RS-232 to RS-485 converter, post details about that device.
 
Hi Ken
many thanks for you replay .... so you say that channel (1) in the ML1500 only can be used for point to point communication , even if it configured as Modbus master ?
 

Similar Topics

Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
85
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
80
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
103
Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
Replies
8
Views
324
Been fighting all morning with a stubborn HMI. It just won´t connect with the plc. attaching from settings. Have i missed anything? Both plc and...
Replies
5
Views
299
Back
Top Bottom