PanelView Plus 1250 restore default config

easystevie

Member
Join Date
Jan 2012
Location
Los Gatos, CA
Posts
1
I am working on a 4 year old PanelView Plus 1250 that does not have the Goto Configuration button on the screen and I would like to reload the program with a CF Card, but I cannot find a way to do this. Is there a way to erase the existing program so that the panel is restored to its default so that I can then reload it with the CF Card?

Thanks,

Steve
 
reboot the screen look on the Left Hand Lower Screen Corner for a small white square
Touch it once - it should brighten
let the screen continue to boot
 
I forgot - if it is not a touch screen - use the F1 Key - i think
 
The white square/F1 function was added around v4, I think, so it's probably present on a 4-year-old terminal.

When the PanelView Plus terminal boots up, it generally runs the *.MER runtime file that it last ran. That file can be on the internal memory, or on the removable CompactFlash storage card.

PanelView Plus terminals will execute "autorun.bat" files, so you can use simple batch files to copy all the *.MER files out of the onboard flash memory and onto an external card, then erase the onboard files. When the PV+ next reboots, it won't find the *.MER file that it expects to run and will default to Configuration mode.

Let's poke around for reference Batch files.... here:

http://www.plctalk.net/qanda/showpost.php?p=328504&postcount=6
 

Similar Topics

Hey guys, I'm at a bit of a loss with a problem I'm having with some PVP 1250s and hoping for some advice. In firmware and application version...
Replies
0
Views
290
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
Replies
0
Views
1,493
Hello, I recently installed an **** Flexy 201 so we could monitor our PLCs (one SLC 500 and one Control Logix) remotely under a VPN. One of the...
Replies
0
Views
2,339
Hi, I have a customer that has an intermittant issue with a PV+ (2711P-T12C6D1) and they would like to replace the PV+ with the latest PV+7...
Replies
3
Views
2,984
I have these PLC and HMI and want to communicate them. I made a program in RSLogix5000 and FactoryTalkViewStudio, tried them out with FT station...
Replies
7
Views
4,406
Back
Top Bottom