Hello,

I have a module that has lost factory calibration settings.

I need to go through the self calibration procedure.

I'm pretty sure its just one page out of the manual that explains
what voltage to apply (mv) during which part of the calibration procedure..

Thanks...

Duane
 
500-5051 Manual

Lancie1,

No its for a Siemens / TI 500 series 500-5051.

And I did receive a PDF copy of the manual from another
forum member for this..

I should have updated this thread to solved..

Its actually several steps with this module as you
first calibrate to 0mv

Then each 10 18 36 and finally 45mv.

This is stored in a 2212 NVRAM chip.
This chip was scrambled so we had to start from scratch.

Thanks for the reply..

Duane
 

Similar Topics

Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
80
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
81
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
79
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
159
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
254
Back
Top Bottom