Kinetix 6000 with Drive Executive (Drive Tools SP)

zitam

Member
Join Date
Jul 2008
Location
Pruszków
Posts
77
Hi,

I'm trying to change some values of Kinetix 6000 drive via Drive Executive software, but drive doesn't accept them. It shows message

" The drive did not accept value (value, for example 3000) for parameter ... "

Values I tried to insert are within the range so this not the problem. I can insert them only when I'm not connected when Sercos card isn't in Control Logix chasis . Does Sercos card has promary over Drive Executive? Where can I change it ?

Best regards,

Matt
 
I meant that Sercos ring is disabled, when PLC was in program mode situation looks similar (I cannot change parameters).
 
Sercos takes precedence

What parameters are you wanting to change? and why?


I think that it may be possible to change some parameters via a MSG instruction but I have never done this.
 

Similar Topics

Good morning guys: we suspect one of the drive in the motion group may have issue, we want to swap the drive. we have compact guardlogix...
Replies
4
Views
2,757
I'm using a Kinetix 6000 to drive a ballscrew. The axis was jogged into the maximum negative soft limit and the drive faulted. The fault action...
Replies
4
Views
8,318
I kept getting Kinetix 6000 servo drive fault of E04 (motor overtemp fault). The servo motor is MPL-B450F. The motor was barely warm, certainly...
Replies
3
Views
9,551
Hey Gentlemen. It seems that 2 to 3 months after we have line upgrades to this type of system that we start getting E19 errors on our Kinetix 6000...
Replies
5
Views
6,698
Hi, I've new problem during the same project. Aux Feedback is used on the machine we are upgrading. TTL encoder is used. It's connected ok...
Replies
10
Views
6,411
Back
Top Bottom