I've inherited several PanelMate 1700 units that I have a question on.

Is it possible to removed the red and white message displays that are near the top of every screen? I can't select the displays or can I find where they are setup at.

If they can't be removed, how can I display messages on them. Currently at run time the area is blank.


Thanks
 
I've not seen any message displayed in that area. They did create a Variable-Sized Display Template to display messages/alarms.
 
There is a difference between messages and alarms. If you have defined high or low alarm levels in a readout template or checked the "ALM" column for any of the states of an indicator template, the alarm condition and timestamp will be displayed in the alarm display area. If the original programmer chose not to use the PanelMate's alarming features, the area is available for other objects. Just make sure that there are no alarms defined anywhere before you use the area. The alarm display is always in the foreground, so any message will overwrite anything else you put there.

You have to be careful in your usage of alarms. In general, the PanelMate only scans the PLC for data necessary to update the displayed page. Alarms are an exception. The PanelMate scans the PLC for all tags associated with alarms regardless of whether or not that tag is on the currently displayed page. Too many alarms can result in slower screen updates.
 

Similar Topics

Hi, i have a panelmate 1700 and i want to upload the application from it (for backup) and i don't know what software to use for the transfert ...
Replies
3
Views
1,672
Hello all, I hope there are some PanelMate aficionados in here. I have a pretty simple question that Cutler-Hammer doesn't seem to be able to...
Replies
3
Views
2,686
Hello, I recently uploaded from a PanelMate 1775T PMPP 1700 color to have as a back up as there has been reports of loss of communication to the...
Replies
6
Views
3,502
i have a pm1700 in start up mode everything passes except for real time clock (the real time clock battery passes) i was wondering what the fault...
Replies
0
Views
2,294
i have a cutler-hammer power pro 1700 panelmate with a watchdog fault on the internal clock i need to replace the internal battery can anyone give...
Replies
1
Views
3,435
Back
Top Bottom