Mark,
I think the ML1100 and 1400 allow online editing and these maybe the only ones in the MicroLogix family that do.
 
The 1100 and 1400 do allow online editing.

Stu,
This is not the current problem since you're using a ML1200 or when using the serial port but since we were discussing Ethernet connected SLCs yesterday now is a good time to bring it up. For SLC 5/05s and Micrologix 1100 and 1400 over ethernet another reason online edits sometimes don't work is an incompatible configuration in RSLinx. In RSLinx go to communications -> configure CIP options and set both the Max Fast Messaging connections pre PLC and Max Slow Messaging connections per PLC to 1 and then click Apply. If you haven't already done so then its something you should do as you proceed with networking those PLCs.
 
Alaric

I have ran across that also on slc 5/05 but bot all of them so I am thinking it is firmware specific. Very strange things happen with this issue when doing online edits.

I got these settings from rockwell but the tech could not explain to me why this was happening or why those changes had to be made on some processors.

Do you have any more detailed info as t why this happens and why those settings help?
 
Here is the knowledgebase article on it. A resource issue, whatever that means
 
Last edited:
Mark,

I don't know why. I just change the CIP settings and go with it because the tech note said so. It worked. I didn't give it much thought afterwards.

Who is this Alaric dude you speak of?:confused:

:ROFLMAO:


Troy
 
Last edited:

Similar Topics

Hi, I have a RSLogix 500 that when I try to go online (ethernet) to a SLC1100, I get this error message. "No response form processor at the...
Replies
7
Views
1,604
Hmmm, Having issues today. Trying to go online with a pair of SLC551 and ML1400 on the same network. I get the message: Diagnostic Status...
Replies
61
Views
23,454
I was trying to modify a program online the other day using RSLogix 500 . The PLC is a SLC5/05. I was online with the PLC, and could change...
Replies
2
Views
5,475
Controller: Micrologix 1500 Hello all, In RS 500 my program will not allow me to make online changes. When I click on the ladder properties, the...
Replies
6
Views
4,916
I am trying to do some online editing in RSLogix 500, however the online edit toolbar is grayed out. The processor (MicroLogix1500) is in Remote...
Replies
8
Views
9,697
Back
Top Bottom