There is a AB Compact Logix L35 PLC in a plant, but the plant people don't know its configured IP address. I want to connect my laptop to this PC and want to take a backup of the PLC program.

To connect Laptop to PLC itself need the existing(unknown) IP Address.

Is there any way to find the IP address of the PLC?
 
Is the L35 actually on an EtherNet network ?, or is the port free ?

You can connect with a serial cable and AB-DF1 driver in RSLinx. From there you can get at the EtherNet port configuration to see the IP Address and the SubNet mask. Set your laptop to the same SubNet mask, and a different IP in the same SubNet, and you can then go online with the EtherNet/IP driver.

Alternatively, you can use a network analyser program (eg. WireShark), to listen to the network data. This is most successful if there is only the laptop and the L35 on the network. You will see originating messages from the L35, but you will have to have a guess the SubNet mask.
 
Hi Daba,

There is PLC, HMIs, PCs etc... all connected to a HUB. So I can connect my Laptop to this HUB. So in this case...

I'm not an expert in networking.
 
What he said...

Connect serially. Get the ip info that you need. Connect your computer to the switch (hub). Be sure to configure your computer to the same subnet and an otherwise unused ip address. If you just enter any ip address under that subnet then you could be stealing an ip from another piece of equipment.


Is the L35 actually on an EtherNet network ?, or is the port free ?

You can connect with a serial cable and AB-DF1 driver in RSLinx. From there you can get at the EtherNet port configuration to see the IP Address and the SubNet mask. Set your laptop to the same SubNet mask, and a different IP in the same SubNet, and you can then go online with the EtherNet/IP driver.

Alternatively, you can use a network analyser program (eg. WireShark), to listen to the network data. This is most successful if there is only the laptop and the L35 on the network. You will see originating messages from the L35, but you will have to have a guess the SubNet mask.
 

Similar Topics

gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
Replies
0
Views
83
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
Replies
3
Views
191
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
229
I was wanting to see if anyone had any information on setting up a cub5 meter and getting the data to a Allen bradley PLC. I think i have the set...
Replies
0
Views
125
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
271
Back
Top Bottom