Ok people here is my problem....Rosemount presure tansmitter scaled 0-200psi reading 140psi at the insturment Via hart. This is about 15ma. Three local gauges confirm that this is the correct presure. The signal is going into a A/B 1794 analog input module, the reading at the card is 8ma. I have powered the loop with a fluke process meter and it reads 15ma. I have simulated the signal back to the DCS through the card and it reads correctly.... 8ma=50psi 12ma=100psi and so on. I have confirmed 24vdc source and even moved the input to an unused one, still have the differance. If I simulate with the hart it does not read correctly and has some bounce. I have checked the cable for a short and found none. I have even gone so far as to run cable outside the conduit between the transmitter and the card just to make sure it is NOT the cable. New cable, same result.The card is full and none of the other Inputs are reading wrong.
What am I missing here? HELP
What am I missing here? HELP