I'm trying to establish serial modbus communication between a panelview plus 1000 and a device for motion control, but I have no experience in this.

I use FTview 6.0 with KepServer running in the HMI project. I think the hmi project is OK (I've just followed the user manual) but I always get an error on the screen in runtime : "Item is no longer available: ModbusRTU.Parker.var_1",where var_1 is the connected variable for a numeric display

I think the problem is the serial cable: in wich cases do I need a null modem cable?

thanks
 
The PanelView Plus terminal has a "DCE" type serial port, while a generic PC has a "DTE" type serial port.

If a null-modem cable works when testing the application on your PC, then you need a straight-through cable to the PanelView Plus terminal.
 

Similar Topics

Currently,we are facing the communication go through with 422 tx+ and tx-. Mitsubishi fx5u series is used and using command rs2. But the package...
Replies
0
Views
101
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,546
MELSEC A RS422 (25pin) <> iQR C24 Serial RS232 (9pin) - Simple PLC Communication Communication from a MELSEC-A Series CPU (RS-422 – DB 25 Pin)...
Replies
4
Views
1,037
Hey guys, I have a problem reading weighing data from AND AD4406 with OP-05 RS-232C Relay and Control input using Rockwell PLC Micro820. I already...
Replies
0
Views
942
I have a zebra barcode scanner connected to a ******* device master UP. They are connected by RS232. By checking the serial logs on the device...
Replies
3
Views
1,134
Back
Top Bottom