saghersiddique Member S Join Date Feb 2012 Location duabi Posts 1 Feb 10, 2012 #1 :smas:I HAVE TO INSTALL A DANFOSS VFD VLT2800 SERIES TO CONTROL THE SPEED OF FEED WATER PUMP TO MAINT THE 5 BAR PRESSURE IN LINE. MY PRESURE TRANDUCER IS 0-10 BAR WITH 4-20 mAMP. IN WHICH PARAMETER I SHOULD SET MY SET POINT.
:smas:I HAVE TO INSTALL A DANFOSS VFD VLT2800 SERIES TO CONTROL THE SPEED OF FEED WATER PUMP TO MAINT THE 5 BAR PRESSURE IN LINE. MY PRESURE TRANDUCER IS 0-10 BAR WITH 4-20 mAMP. IN WHICH PARAMETER I SHOULD SET MY SET POINT.
chelton Member C Join Date Jan 2012 Location melbourne Posts 320 Feb 10, 2012 #2 Assuming you have par 100 set [3] process closed loop, your setpoint can either be set remotely using Analogue input 1, or local from the LCP. Set the setpint limits in par 204 and 205.
Assuming you have par 100 set [3] process closed loop, your setpoint can either be set remotely using Analogue input 1, or local from the LCP. Set the setpint limits in par 204 and 205.
jvdcande Member Join Date Apr 2002 Location Menen Posts 2,178 Feb 10, 2012 #3 And be sure to set the right typeface. If you put your setpoint in capitals, your pump might end up screaming at you.
And be sure to set the right typeface. If you put your setpoint in capitals, your pump might end up screaming at you.
Baranyk Member B Join Date Jan 2012 Location Central PA Posts 57 Feb 10, 2012 #4 jvdcande said: And be sure to set the right typeface. If you put your setpoint in capitals, your pump might end up screaming at you. Click to expand... But if he sets the font too small, he might not be telling it loud enough, and it might not listen to him.
jvdcande said: And be sure to set the right typeface. If you put your setpoint in capitals, your pump might end up screaming at you. Click to expand... But if he sets the font too small, he might not be telling it loud enough, and it might not listen to him.