BACnet and Modbus Communications
Chiller data that can be read and modified using
specific BACnet or Modbus Register Addresses; and
the data associated with the addresses, is outlined in the
following description:
ANALOG WRITE POINTS
This data can be read and modified using a BACnet or
Modbus network connection. The Modbus Register
Address for these points is 1025 + AV #.
BINARY WRITE POINTS
This data can be read and modified using a BACnet or
Modbus network connection. The Modbus Register
Address for these points is 1537 + BV #
ANALOG READ ONLY POINTS
This data can be read using a BACnet or Modbus
network connection and can NOT be modified using
this connection. The Modbus Register Address for these
points is 513 + AI #.
BINARY MONITOR ONLY POINTS
This data can be read using a BACnet or Modbus
network connection and can NOT be modified using
this connection. The Modbus Register Address for these
points is 1281 + BI #.
Communications Data Map Notes
(See Table 44)
1. IPU II based units are configured for Native BACnet
MS/TP and Modbus RTU communications.
MicroGateway or E-Link not required for these two
communication protocols.