karivelm Member K Join Date Nov 2006 Location Quebec Posts 66 Feb 20, 2012 #1 Is it bad pratice to use one output from a PLC to control 2 lights.. Should I use a relay? Or can I put both lights in parallel direclty on the output of my 140DAO840-00
Is it bad pratice to use one output from a PLC to control 2 lights.. Should I use a relay? Or can I put both lights in parallel direclty on the output of my 140DAO840-00
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Feb 20, 2012 #2 As long as you don't exceed the current rating of the output module you can put as many lights as you want. See pdf below for info on your output card. Last edited: Feb 20, 2012
As long as you don't exceed the current rating of the output module you can put as many lights as you want. See pdf below for info on your output card.