AB550 Panelview woes

308sparks

Member
Join Date
Mar 2012
Location
Nebraska
Posts
2
I am trying to connect an AB550 panelview with a RS232(DH485)port to my already existing DH485 network. The comm lite on the panelview blinks but the fault lite is off. I am trying to upload the program that is currently in the panelview. I am using a PIC that is connected to my computers' serial port as the AB manual states you must use a PIC driver to communicate with the panelview. I have tried to connect to the panelview using null modem cables to an AIC plus that is on the 485 network but I cannot get the panelview to upload and I am not sure if my cabling is correct or what is going on. Any help would be greatly appreciated.
 
Please give us the complete catalog number of your PanelView. I am a little confused about which PV you have.

Use a straight thru cable between the PV and the AIC. See pdf below


Baud rates must be the same and node addresses must be different.
 
Last edited:
Mickey:
The panelview number is 2711-K5A5, FRN 3.13. Does the panelview need to be connected to a PLC to upload what is in there now? There is a conveyor screen which comes up as soon as the P.V. is powered up. I cannot see the P.V. on the DH485 network and I have looked in all the AB Panelview manuals I can find to see if they show exactly how the Panelview should be connected to a DH485 network. The panelview has only one RS232 port, no printer port. Any help will be greatly appreciated.
 
Does the panelview need to be connected to a PLC to upload what is in there now?

No

You can connect to the PV's RS232 port from your PC using a straight thru cable. ( see my previous post above). Then using the 1747-PIC/AIC+ driver in RSLinx. You will need a real serial port to use this driver. See PDF below for more on this driver.

If you don't have a real serial poprt the a 1747-UIC ( USB to DH485 converter) will work. Or use a memory card to uplaod/download the PV's program.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
78
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
53
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
167
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
77
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
105
Back
Top Bottom