Hi All,

i am trying to get a backup of several machines at the plant over ethernet. each machine has several ethernet devices and a individual ethernet switch. the machines are not connected together.

i looked at the plc program and found the ip address and set my laptop to the main numbers but with a different last number. submask of 255.255.255.0.

trouble is, my rslinx pro does not see the plc.
i also cannot get onto the plc with logix 5000 via ethernet.

I CAN connect via serial port and download the program and did confirm the ip address. its the same as the one i had.
i just used my ethernet cable 5 minutes before and have had it tested and have confirmed its ok.

I am trying to learn the logix 5000 software and have been able to connect to other plc's in the past.

All comments welcome!
thanks in advance,
james
 
Open a command prompt and try to ping the plc IP address or the address of some of the other devices to make sure you have a connection.

Are you connecting to a switch? The switch may have MAC address filtering meaning the switch will not pass traffic from your laptop if the MAC ID number of your network card is not in the list in the switch.

What linx driver are you using? The ethernet IP driver or the ethernet devices driver. The ethernet devices driver you must type in the addresses of the device you want to comm with.
 
If linx does not see the plc then logix will never connect as it connects through linx. Concentrate on getting ping working because it is the lowet level comms you have in your aresenal.

If you can't ping the plc then noting else is going to work.

If you have windows firewall or antivirus on that laptop turn it off as it can impede traffic. The windows firewall is known for this.

You can setup exceptions once it is working but turn them off until you get things running.
 
What type RSLinx driver are you using?
An EtherNet/IP driver configured for a PC network card having the same first three "numbers" of the IP Address of the bridge managing the subnet the PC is patched into will return (when browsing)the icons of all the subnet's active/connected devices.
An EtherNet driver used within the same scenario as the one previously described, will return only the addresses entered at the driver's configuration time.
I would first make sure you are using an EtherNet/IP type driver when trying to connect to the subnet.
 
i am using ether net not the ip driver.
I retyped in the addresses of the ethernet device with no success.
I then changes the ip address of my laptop from x.x.x.235 with submask of 255.255.255.0 to x.x.x.186 and it worked.

only two ethernet devices on this machine.
why would changing the address from 235 to 186 matter?

regards,
james
 
With that subnet anything from 1 to 254 that is not taken should be fair game. An ip conflict should have thrown an error, try pinging 235 now to see if you get a response.
 

Similar Topics

Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,592
Hey everyone! So I'm trying to get different data from my Eaton DG1 VFD to my studio project. So far my research has led me to something called...
Replies
10
Views
1,557
We have a cell that was done by an integrator. It has lots of intermittent comms issues that sometimes are minor and sometimes doesn't allow you...
Replies
5
Views
1,282
Hey everyone, working with an ABB drive for the first time, and I've found the sample programming that ABB provides for communicating with a...
Replies
11
Views
4,300
Anyone ever set up communications like this? Trying to assist a plc instructor with making a lab up for a local junior college. They have both...
Replies
5
Views
4,354
Back
Top Bottom