Slc 5/05 1747-l552

berrabbit5849

Member
Join Date
Nov 2011
Location
Daingerfield,Texas
Posts
117
I am looking for all the componets to put in a system using remote I/O. I think I need a 1747-SN scanner module. Do I need one for each remote rack? I think I need a 1747-ASB for each remote rack? Will only be doing remote I/O. Do the scanner and ASB connect via Blue Hose ? I want to connect a PC to the processor at all times for troubleshooting. Does the processor have a ethernet port for this or is it another card.
 
I think I need a 1747-SN scanner module. Do I need one for each remote rack?

No, only the rack with the processor.

I think I need a 1747-ASB for each remote rack?

Yes.

Do the scanner and ASB connect via Blue Hose ?

Yes, make sure you have termnation resistors at each end of the network.

See link for the manual below.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um013_-en-p.pdf

Does the processor have a ethernet port for this or is it another card.

Yes. It also has a serial port.
 
Last edited:
Btr btw

On my remote racks will I have to program a BTR and BTW to communicate with these. Can you show me an example ? It has been a long time since I have done this. Also there was something about a "G" file to fill in.
"
 

Similar Topics

I have a system that was upgraded from an AB SLC5/04 to a 5/05 Ser C. Rev A. Opsys is OS501 ser c. Frn 11. The E-net connection is slow as a...
Replies
1
Views
1,403
I upgraded from a PLC 551 to a 552, to go from 16K to 32K memory. Everything works fine except that RSlogix tells me I have reached the memory...
Replies
4
Views
3,478
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,592
I have the following Items connected for DH-485 per the drawing. SLC 5/03 HMI: Automation Direct EA9-T10CL+13Y19B054 1747-AIC #1: connected...
Replies
10
Views
3,046
Hello, First I looked at Manuel and Plctalk but I did not find or maybe not understand. How I can connect ''HTL / Push pull-24 volt encoder'' to...
Replies
4
Views
2,522
Back
Top Bottom