APC UPS to WinCC flex...

Kasperv79

Member
Join Date
Mar 2012
Location
Copenhagen
Posts
48
Hi.

Ive tryid searching in here and around the web but without luck..

My question is HOW to get the APC-UPS (SMARTUPS 300XL) USB or serial connection to activate a script in WinCC Flexible ?? is it possible?


Information:

WinCC flexible 2008 adv. SP2 running on a Win 7 Ult 32bit.
connection through Ethernet to a CPU 317-2 PN/DP.


//kasper
 
Are you talking about a digital signal? from the APC?

there is no digital outputs on the APC only an "EPO" connecter for emergency remote dicharging...
 
You have a slot on the back of the unit for a expansion card. Use this to connect as jesper has said http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9610&tab=documentation

The serial and usb connection is just a link to the powerchute software which will do a controlled shutdown of connected computers when the battery level reach 2% left.

There is a java enviroment that could be used to do other things but the java code you will have to "roll your own".
 

Similar Topics

Please tell me how to correct two alarms on APC Galaxy 3000 UPS: #1: Cooling fault (Cooling liquid level is low) #2: End of batt service life Due...
Replies
2
Views
1,429
This is a program in a machine that has been running for about 7 years without any issue like this. We have a master servo (the machine's main...
Replies
3
Views
1,163
If f.i. the slave axis has to start the camming not from the beginning of the cam but somewhere in between, the parameter 'cam lock position' has...
Replies
0
Views
1,414
In a Siemens controller when I have a cam where f.i. master- and slave position is absolute, when the the camming is started the slave will first...
Replies
0
Views
1,595
Hi has any one linked a Schneider Electric Smart UPS to a PLC through Modbus TCP? Supposedly it can do it, I'm told. but I'm not entirely sure...
Replies
3
Views
2,412
Back
Top Bottom