PLC to HMI Station communication error code 0x80000104

khutto2012

Member
Join Date
Mar 2012
Location
Tripoli
Posts
4
PLC to HMI Station communication Problem _ error code 0x80000104

This happened when the PLC was not working for almost a year.. When we try to start the system found ###### at HMI and the Bus fault signal is BF is blinking yellow
 
Normally, I would ignore a thread with such poor description of the problem.
But since you are from Libya and the 1-year down period may be due to recent problems in your country, I shall try to help.

The message just say that there is no connection from the HMI to the PLC.
If I were in your situation, I would start with loading the program in the PLC from scratch. And depending on how it goes, I would investigate the diagnostics buffer and the Hardware diagnostics to find out what else may be wrong.

You can also help by describing in much more detail what your system consist of and what it does.
 
Thanks a lot Jesper, I do appreciate your quick response, As of this moment i still gathering all the details at location, how and what are the status of the signal at PLC and HMI. Will advise ASAP.
 

Similar Topics

Hi, I have a SIMATIC 416-2 CPU connected to a MP 377 WinCC touch screen via MPI cable. How do I detect a communication fault on the MPI cable...
Replies
3
Views
7,200
Hello people. Me and three others are doing our final exam projects and have will be programming a 313C CPU. Connected to this CPU is a touch...
Replies
1
Views
5,982
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
Replies
1
Views
72
Hi, I'm thinking about using commands for Melservo J5 controller via HMI without PLC. Have you guys done this kind of control configuration for...
Replies
3
Views
139
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
116
Back
Top Bottom