kittydog42
Member
I have a system with the following:
1769-L35E::1769-PA2::1769-IQ16::1769-OB8::1769-IF4::1769-OF2
I went to the job on Monday and found the processor in a major fault. I didn't capture the exact error but it pointed to the OF2 analog output module. The "OK" light on the OF2 was not on at the time. I powered the system down and removed the module, checking the connections. They all looked good. The switch was properly set for internal bus power. The endcap looked good as well. The "OK" light came on upon power-up but eventually turned off again. I called RA and they suggested that I exercise the power selection switch in the module, so I did that. After that, the "OK" light seemed to stay on. I unchecked "Major Fault On Controller If Connection Fails While In Run Mode" for all of the local I/O and left the job for the day.
The next day I got a call that there were problems. The guy on site opened up the panel and noted that "a red light was blinking" on the PLC. He also indicated that the "OK" lights were on for the analog modules. I tried to get remote access and couldn't, but eventually got another vendor on site to connect and report the fault reading to me. Here it is:
(Type 03) I/O Fault
(Code 16) I/O module connection failed on required module.
Port: Backplane
Module: <unknown>
Error: Connection timed out
Info: <none>
Have any of you seen this come up or know what I should look to replace? My local distributor suggests just the OF2 module, but the engineer at RA I spoke with seemed to think I should replace everything, which is probably not going to be possible due to budget and logistics. The RA engineer seemed to have a low opinion of CompactLogix and acted as if this was to be expected due to the "commercial quality" of the line. That's not how the RA sales team described it when they convinced us to switch over! The bottom line is that if possible, I'd like to try to find a solution that I can feel confident in since the job (of course) is not local or convenient.
1769-L35E::1769-PA2::1769-IQ16::1769-OB8::1769-IF4::1769-OF2
I went to the job on Monday and found the processor in a major fault. I didn't capture the exact error but it pointed to the OF2 analog output module. The "OK" light on the OF2 was not on at the time. I powered the system down and removed the module, checking the connections. They all looked good. The switch was properly set for internal bus power. The endcap looked good as well. The "OK" light came on upon power-up but eventually turned off again. I called RA and they suggested that I exercise the power selection switch in the module, so I did that. After that, the "OK" light seemed to stay on. I unchecked "Major Fault On Controller If Connection Fails While In Run Mode" for all of the local I/O and left the job for the day.
The next day I got a call that there were problems. The guy on site opened up the panel and noted that "a red light was blinking" on the PLC. He also indicated that the "OK" lights were on for the analog modules. I tried to get remote access and couldn't, but eventually got another vendor on site to connect and report the fault reading to me. Here it is:
(Type 03) I/O Fault
(Code 16) I/O module connection failed on required module.
Port: Backplane
Module: <unknown>
Error: Connection timed out
Info: <none>
Have any of you seen this come up or know what I should look to replace? My local distributor suggests just the OF2 module, but the engineer at RA I spoke with seemed to think I should replace everything, which is probably not going to be possible due to budget and logistics. The RA engineer seemed to have a low opinion of CompactLogix and acted as if this was to be expected due to the "commercial quality" of the line. That's not how the RA sales team described it when they convinced us to switch over! The bottom line is that if possible, I'd like to try to find a solution that I can feel confident in since the job (of course) is not local or convenient.