transformer sizing

matlark

Member
Join Date
Jul 2011
Location
KY
Posts
102
If I have a load of 600VA and undersize the transformer to a 500VA transformer (square d) would I be in an acceptable range? I know there is a fudge factor with sizing xformers.

THanks
 
Depends how long you want the transformer to last...

NEVER undersize a transformer. ALWAYS oversize it!
 
Transformers 101

If I have a load of 600VA and undersize the transformer to a 500VA transformer (square d) would I be in an acceptable range? I know there is a fudge factor with sizing xformers.

THanks

Actually, there is no "Fudge Factor". A Transformer is one of the things that you can count on for 100% ampacity, for 100% duty cycle.

If you have a 600va load, you will never get there with a 500va transformer.

What is your application? 500va is only 1/2 amp at 120vac.

If you are working on ONE machine, buy a transformer with spare capacity. If you are engineering a purchase for 10 or more machines, then you must understand your load, and size the transformer for adequate capacity, and economics in design.
 
A 500VA transformer CAN supply more than rated, possibly 600VA or more, but only for very short amounts of time. The amount of time depends on the cooling you can provide and the overload VA you are trying to get.

But in anycase, building from new, always err on the side of caution and upsize. You never know who will come along later and start adding more loads to a maxed out transformer.
 
My experience is that while power transformers will generally have a fairly conservative rating small control transformers do not. In addition it is quite common for people to install these transformers without really considering the cooling requirements. Deliberately overloading this type of transformer for long periods of time is a recipe for a fire.
 
As the rating is VA (Volts x Amps) the performance is relative to the Power factor of the AC load.
the Idea of doing load calculations is to protect your transformer.
As you excede the VA ability of the transformer you create other problems.
Apart from the fire risk, a 600 Watt load is not 600 VA, so why would you attempt to use a 500 VA Transformer
 
Actually, there is no "Fudge Factor". A Transformer is one of the things that you can count on for 100% ampacity, for 100% duty cycle.

If you have a 600va load, you will never get there with a 500va transformer.

What is your application? 500va is only 1/2 amp at 120vac.

If you are working on ONE machine, buy a transformer with spare capacity. If you are engineering a purchase for 10 or more machines, then you must understand your load, and size the transformer for adequate capacity, and economics in design.


Actually, 500va is just a hair over 4amp (4 x 120 = 480) and it is 1A on the 480V side
 

Similar Topics

Sorry, not really PLC's. I have been going around and around trying to get a solid answer to my question and not finding anything that really...
Replies
15
Views
4,917
I have an application that has 3 24VDC motors. Each motor pulls around 10 amps, but none of them will run at the same time. If I fuse them...
Replies
20
Views
5,751
Been a long time since i have done any actual electrical design and want to make sure i am doing this correctly. I have 480VAC 3 phase available...
Replies
3
Views
1,547
Hi Everyone, I am a student and am new here and I have a question that is not a plc topic. I would like to know how to go about sizing fuses on...
Replies
9
Views
3,848
When using a transformer sizing tool like this http://www.csgnetwork.com/xformercalc.html when it ask if it's a single phase or 3 phase how does...
Replies
13
Views
4,687
Back
Top Bottom