DH485 set up question

adamdayno

Member
Join Date
Mar 2012
Location
kingston
Posts
8
Hi all,
If you were given these circumstances what would be your advice to do with this old equipement.....throw out and start over is unfortunately not an option.
I have (10) 5/03's each set up with its own PV600. The request is in to pull data from each and do it as cheap as possible. So I'm thinking DH-485 with 1747-AIC at each machine. Oh total distance is only about 300'. The supervisor of the department wants a PV in his office to be able to view the data.......Yes I would rather put in into excel or something but i lost this battle.
would you guys do the same with what I'm handed?
Thanks
 
Are the PanelView 600 terminals connected to the SLC-5/03 controller's Channel 1 DH-485 network port or to the Channel 0 RS-232 serial port ?

You'll either use 1747-AIC isolators to network the controllers' Channel 1 ports, or use 1761-NET-AIC isolators to network the controllers' Channel 0 ports.
 

Similar Topics

Hello all, i have seen a few things here and there about connecting to a panelview 550, however i still would like to ask a few things, I have...
Replies
6
Views
133
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
Replies
5
Views
886
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
Replies
1
Views
671
Hi, I have a SLC5/03 connected to a working HMI via RE232 port, and connected to a broken HMI via DH485 (RJ45), I want to use the cable that used...
Replies
15
Views
3,283
Hey all, long time reader but first time poster here. I've been tasked with an odd one and was wondering if anyone else had experience in this...
Replies
17
Views
5,350
Back
Top Bottom