Just to make the numbers easy...if I have a ML1200 driving 10 amps (various small motors and solenoids) I would need to fuse the secondary side of the transformer at 12.5A? Used 125% since above 9A.

thanks
 
not certain what knowledge you have.
you should have regulations for wiring equipment like this. - maybe not.
Understanding the load of a control circuit is very important
In a non PLC environment it is common practice, here, to calculate maximum demand. similar to the total number of devices that can be loaded at the same time.
This is slightly different, but, consider the types of motors/solenoids and their magnetising/starting currents.
you will need to take this into your calculations or you may suffer false tripping of circuit breakers. HRC fuses, not commonly used any more,need to carefully sized as well.
 
Neglecting the fact I may need fusing on each output, diodes, etc... would fusing the secondary at 12.5A be sufficient.
 
I would definately not use the PLC output to directly switch a 10 Amp load.
3 Amp resistive only
 
Each plc output can output a max of 2.5A, so a small motor, solenoid, etc should be fine, but getting off topic.
 
When fusing motors and solenoids you may want to look at slow-blow fuses to accommodate the inrush. I've found that saves some nuiscance fuse blowing.
 

Similar Topics

Engineers and designers, question. Do you typically fuse the PLC outputs ? I see some that are fused and many that are not. I typically fuse...
Replies
3
Views
1,021
I know it's a good idea to fuse the individual outputs from a PLC and possibly better to isolate with interposing relays. But, is ther any...
Replies
7
Views
4,691
I'm putting together a new PLC setup (perhaps my most complicated one so far) and have some questions about fusing. Lets start at the beginning...
Replies
11
Views
11,521
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
26
Hello, I'm trying to delve a little into rs-485 communications for a couple projects of mine. Until now I've been using a delta vfd and a delta...
Replies
2
Views
46
Back
Top Bottom