SDM_VUT Member S Join Date Apr 2012 Location Utah Posts 4 Apr 12, 2012 #1 Hello, Can tell what Logix 500 software version I need to add a 1747-AENTR to my SLC rack. Thanks ahead.
Hello, Can tell what Logix 500 software version I need to add a 1747-AENTR to my SLC rack. Thanks ahead.
The Plc Kid Member Join Date Feb 2009 Location Macon, Georgia Posts 3,233 Apr 12, 2012 #2 You don't use 500 you use 5000 V20.
SDM_VUT Member OP S Join Date Apr 2012 Location Utah Posts 4 Apr 12, 2012 #3 You don't use 500 you use 5000 V20. Click to expand... You cant configure a SLC rack with RS 5000.... You do know you can get this card for either system...
You don't use 500 you use 5000 V20. Click to expand... You cant configure a SLC rack with RS 5000.... You do know you can get this card for either system...
The Plc Kid Member Join Date Feb 2009 Location Macon, Georgia Posts 3,233 Apr 12, 2012 #4 SDM_VUT You are terribly misinformed or you have your part numbers confused. 1747-aentr gives you the ability to master slc over ethernet for compact or controllogix. This module replaces your slc processor. In no way does it work with it. Take a look here http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/migrat-pp004_-en-e.pdf
SDM_VUT You are terribly misinformed or you have your part numbers confused. 1747-aentr gives you the ability to master slc over ethernet for compact or controllogix. This module replaces your slc processor. In no way does it work with it. Take a look here http://literature.rockwellautomation.com/idc/groups/literature/documents/pp/migrat-pp004_-en-e.pdf
Helliana Member H Join Date Nov 2011 Location Louisiana Posts 801 Apr 12, 2012 #5 Says exactly what PLC Kid stated in chapter 1 of the users manual. http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um076_-en-e.pdf
Says exactly what PLC Kid stated in chapter 1 of the users manual. http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um076_-en-e.pdf