SLC 5/04 and DH+

angi

Member
Join Date
Jan 2010
Location
us
Posts
361
Hi Guys

There is a DH+ Network with some SLC 5/04 on it, I could see all of SLCs, but could not update the code through the DH+, I checked the manual, know that the 3-pins DH+ connection only for communication, if I want to download the new code, I must use RS323 or the round DH+ connection, is that right?

Thanks
 
No, if you can connect thru the DH+ then you can also download/upload or do online editing of the program of all on the network.

What error did you get when you tried to do this?
 
I got X4 error when I try to download a new code.

Sorry angi but I don't know what that means. Hopefully one of the AB gurus will.

Is there a description that goes along with the error?

Are you able to download thru the serial port?
 
Code:
0004  = A run time memory integrity error occurred. This is a non-user error.
 
1)Cycle power and then re-download.

2)Check grounding and surge suppression

?? Just a wag from the manual/help
 
Does anyone know why my slc5/04 keeps reverting to a baud rate of 1200. I have gone into chan 0 and set it to 19200, but when I autoconfig it changes back to 1200!!!!!
 
Can you tell us exactly how you are changing the baud rate online/offline. Be as detailed as possible.

Are you getting a warning message after changing it? See picture below.

Are you then clicking on "Apply"?
 
Can you tell us exactly how you are changing the baud rate online/offline. Be as detailed as possible.

Are you getting a warning message after changing it? See picture below.

Are you then clicking on "Apply"?

Mickey thanks the pennies dropped! catch you later.

Eddie Chttp://www.plctalk.net/qanda/images/smilies/thumb.gif
 

Similar Topics

I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
92
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
97
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
93
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
76
Back
Top Bottom