hi to all!!


may i ask something. i have a 40 I/O micrologix 1200 1762 L40BXB. and i have a keyence switching power supply with 1.6A 24V output. so if i calculate it, i have a 38W power supply yes? the L40BXB wattage requirement is 37Watts. is it ok if i use the 1.6A power supply? or do i need to need a higher wattage power supply? and what if i connect 1pc of 16 input module and 3pcs of 16output modules, will it require higher wattage with this config coz i cannat seem to find wattage requirements for individual modules? thanks in advance!!


jomar
 
look at the specs of the plc - power requirements.
watts = volts * amps.

i would put a power supply twice the size you specified. you are loading the power supply to close to the max.

if you add i/o to the power supply, you must know what the sensor power requirements are. i typically use 12ma for inputs. you must look at each output device. if its a coil, add extra for surge current.

regards,
james
 
I agree with James. If we don´t know the quantity and type of sensors used (inputs) and the type of outputs (relays, valves, motor starters etc.), we can´t help you choose the correct power supply. If I were you, and since it looks like you are having some difficulty, I would play it safe and go for 3 A PS. The 1.6A PS is too SHORT.
 
Theoritically it can work, however your power supply must only be connected to your main cpu.all incoming and outgoing from the inputs and outpus must be separated.

Cheers,
 
i got a 6.5A omron PS instead. :)


Way to go(y)

If in doubt on power supply size check the price of a supply that is double the size
remember VA (As Stated above) and coil inrush currents
(approx 3 times holding current)
 

Similar Topics

Hi, guys. I am what you would call the Lord of Newbies regarding this. So, please bare with me. I work in an airport handling company in the...
Replies
13
Views
3,190
Good morning Gentlemen, This is my first post and I need some serious advice. Firstly I want to say I am not a PLC programmer nor do I wish to...
Replies
31
Views
8,631
I have come across a six lead motor that has been rewound, and is missing the U1,V1,W1, U2,V2,W2 identifying tags on its leads. Is there any way...
Replies
12
Views
4,303
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
79
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
87
Back
Top Bottom