Hi

I am working with RSLogix redundant system.Please find my project in attachment.My redundancy is working ok,ie,when I switch OFF, one CPU,other is becoming master and reverse.

But I am not able to see IO cards.I have two rack of IO.IO rack is connected over controlnet cable .Do I need RSNetwork Controll net software?

:unsure:

Thanks and expecting some answer .
 
Last edited:
1) get your IO to work without redundancy
2) Make sure that the Cards are the same - Same Hardware, Same firmware
3) make sure that the Redundant control net addresses are at high contorl net addresses


Yes you must use control net software to schedule the network
 
Ambrish,
you have analog I/O in the remote rack (1756_IF8H), but the controlnet card is configured for Rack Optimization. When you use analog, they should be direct connections not Rack Optimized. So I think you need to delet the cards and controlnet card and put them in again. When you put the Controlnet adpater back in, dont select rack optimized select none. This will raise your connections as each card will be a connection instead of 1 connection when using Rack Optomized. The best thing to do is place all your non analog cards under one controlnet adapter as Rack optomized, and place all the analog card under the other controlnet adapter. This way you can make one card rack optomized and the other as none. This will reduce the connections if it becomes an issue.

First try deleting and instaling again as non rack optomized the way you have it. You will need Controlnet software to schedule the connections. See if that helps
 

Similar Topics

Anyone know how to un-dim the "Use Wildcards" box in RSLogix 5000's Find-function? The help file says "Use Wildcards appears dimmed if you have...
Replies
11
Views
5,150
Good afternoon, I have a question with the Allen Bradley 1756-L83E. If I have multiple I/O cards (120VAC, 24VDC input output and analog cards)...
Replies
2
Views
672
I have a project where I will need around 20 IO cards. I'll probably have 5 on a compactlogix L320ER and 15 or 20 on a Point IO AENTR module. The...
Replies
4
Views
968
Hello folks I am newish to controls and even newer to Omron. I have two OC211 cards on an Omron cj2m-cpu33 that are not receiving power from the...
Replies
2
Views
766
I am trying to 'standardize' several HVAC units running micrologix 1400. My question: Can I 'leave out' IO cards in the IO map below or do I...
Replies
4
Views
1,509
Back
Top Bottom