Ah, youth and it's affection for brevity.
I think you're talking about sending data from a PLC-5 to a ControlLogix controller using DH+ protocol.
This is discussed in detail in the 1756-DHRIO module user manual, and in about fifty different Knowbase articles that I found by using the keywords "DH+ and ControlLogix and PLC-5".
There are two basic principles to master:
1. Because the ControlLogix uses a Tag-based memory system instead of a PLC-5 Register-based memory system, some equivalency table must be set up between the two memory systems. This is defined in RSLogix 5000 in the "Logic -> Map PLC/SLC Messages" menu. I usually define an Array of INT or REAL data to match the PLC-5 File number for Bit, Integer, or REAL data that I want to exchange.
2. Because the ControlLogix CPU and the 1756-DHRIO module can reside in different slots of a 1756 chassis, there is another step in addressing a DH+ message besides just the Target Node. If the Target Node is all that is specified in a Local DH+ message from a PLC-5 to a ControlLogix, then the message will be routed to the Slot number defined as the "default Controller Slot" in the 1756-DHRIO setup (right-clict in RSLinx WHO to set this up). If messages must be routed to other slots in the Logix chassis, then a Routine Table must be set up with Link ID's for everything.
Remote DH+ Link addressing is too complex a topic for a discussion board, so I will refer you again to the 1756-DHRIO module user manual and the
http://support.rockwellautomation.com knowledgebase.