Hi, I'm literally brand new to using PLCs, this is my first day trying to work with them. I'm using a Micrologix 1100 unit and RSLogix 500.
My current issue is that I don't know how to program a switch in the ladder logic that closes when the analog input's voltage is over 150 mV. As my understanding of PLCs is minimal at best, I don't really know if this can be done or if there's a better way of doing this. If anyone could provide some suggestions, it would be greatly appreciated.
Thanks.
 
It should look something like this. The comparison value needs to be adjusted for the correct range of your input module. For example, if you have your analog input module configured for "0-10 VDC" and "PID Units", then a value of "234" would equal 0.150 volts or 150 milivolts.

ANALOG INPUT.jpg
 
Last edited:
Thanks a ton! I'm still having some difficulties getting it to work properly, but I think that's just because I have the inputs and outputs labelled incorrectly or something, but at least I'm going in the right direction now.
 
Looking at the MicroLogix 1100 Instruction Set Reference Manual, if all you have is the built-in analog inputs, then they will be addressed as I:0.4 and I:0.5.

Your Mircologix 1100 analog input values are converted to 150 milivolts like this: .150(1023)/10 = 14.66 = 15 Integer.

ANALOG INPUT R1.jpg
 
Last edited:
I am pleased to help, but many on this site will tell you that I am neither a gentleman, or a scholar. :cry:
 

Similar Topics

Hello, This should be an easy one for all the experienced hands out there... I have a AB PLC running on a mobile unit that has 12 VDC batteries...
Replies
7
Views
2,734
Hi Team I need your advice please, what are the consideration of selecting control voltage levels in a PLC and I have already make my mind to...
Replies
5
Views
2,837
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
136
I've got 6 identical regenerative vacuum blowers powered by 6 identical drives in 3 identical panels all fed from the same 1 main building feed...
Replies
27
Views
876
Hi all, We are currently experiencing an DC over voltage fault on one of our inverters. During commissioning a snag was raised whereby excess...
Replies
0
Views
190
Back
Top Bottom