hello all i have a question relating to circuit protection. my understanding is that 99% of molded case circuit breakers are inverse time trip. I have several that say instantanous trip CB on them? and many more with nothing at all but the current rating on the handle. whats the best way to tell by looking at them?

Thanks
TL
 
Yes inverse time -just like with fuses. If the ratings are not on the unit itself then you will have to look up the factory manual / documentation.

Dan Bentler
 
It depends very much on the moulded case circuit breaker. I do not know if you are referring to small or larger ones.
I use a lot of Schneider MCCBs from about 63 amps up to 1600A or more and they all have separate trip units. There are many settings in the trip units with respect to current including instantaneous, long time, short time,earth leakage etcetera. Different trip units have different capabilities.
 

Similar Topics

Hello everybody. My company has asked me to take a 480vac delta to 208vac wye Xmfr and wire it backwards to get 480vac 3 phase from 208 3 phase. I...
Replies
16
Views
6,201
Hi all, After starting a new job and convincing management of the need for a scope they have so generously allowed a poultry AU$700 to play...
Replies
8
Views
3,330
Good Morning , I am now in somewhat of a project management role with our corporate office ,and was once very involved in plant...
Replies
5
Views
3,436
Hello guys, I would need some help. I have installed the aveva plant scada and want to run a project. From the configurator, all are fine, as I...
Replies
0
Views
97
I want to establish a Profinet network in my production plant to connect multiple devices, including a PLC, HMI, and multiple Profinet-based...
Replies
19
Views
648
Back
Top Bottom