ControlLogix as a gateway

whumphrey

Lifetime Supporting Member
Join Date
Aug 2011
Location
Lincoln, NE
Posts
35
I have an application where I need a CompactLogix on one network to communicate with some Ethernet/IP valve actuators on another network.

My idea is to put in a ControlLogix chassis with two Ethernet modules to act as a gateway between the CompactLogix processor and the the valve actuators.

Will I be able to configure my CompactLogix program to see the valves via the ControlLogix ethernet modules this way?

Thanks,
Warren
 
Not as an I/O connection.

There can be only one backplane between a ControlLogix-family controller and the network interface module that's connected to an I/O network.

To put it another way: "You can only scan I/O on local networks".

The CompactLogix can send unscheduled Messages to the valves, but it cannot control them.

Here's the bad part: You can configure this and it *might* work, until the planets stop aligning and the connection gets reset. I've been through this a few times with users who set it up against my advice, and it worked for a while, and I had to explain the technical definition of "coincidence". This is not a supported or recommended connection method.
 
Thanks. What do you mean by *control them* ? Can the *unscheduled messages* read and write data to the input and output image of the valves?
 

Similar Topics

Hello all, I am looking for a device to read OPC UA and populate the controllogix tags. So I need a OPC UA client to populate the Controllogix...
Replies
8
Views
2,725
Hello forum members! It's been quite a while since I programmed and installed a PLC but did quite a bit in the late 90's. Back then it was RS...
Replies
11
Views
5,131
Good Morning from the "Waist Deep in Snow" Mid Atlantic. I have a question about the 2) options that ProSoft has for Ethernet/IP to BACnet/IP...
Replies
4
Views
4,430
We are replacing a PLC3 with a new ControlLogix. There is an existing mainframe application that communicates with the PLC3 via a 1770-KF2 (DF1...
Replies
1
Views
2,379
Trying to determine the correct Path for a read by a ControlLogix L-62 from a PLC-5/60B residing on 1756-ENET Gateway, Channel A, PLC 01...
Replies
1
Views
4,039
Back
Top Bottom