analog input show half range

iranshahi

Member
Join Date
May 2012
Location
tehran
Posts
9
hi my freinds
i have an analog input modul of siemens by order 6es7-7kf02 .. that configur by 315-2dp cpu
despite the configuration of channel 1&2 is together but the firs chnnel of this modul shows half range.
channel 2 work exactly.
wher is my problem???:unsure:
 
Maybe the problem isn't the Analog Input module, but the Transmitter configuration.

No
I'll test both channels with one transmitter.
The first channel shows half the range.
While the two channels with the same transmitter is working correctly.
 
Maybe the wiring to the first channel is different from the wiring to the second channel. Maybe one channel is wired for a 2 wires and the other is wired as 4 wires.
Are you connecting the transmitter directly to the AI card, or are you making the connections to terminal blocks already wired by someone else?
 
i'm checked hordware configuration and set the parameter to 2wire curenc.
I did all the correct setting
The module has been corrupted???
 
When you search for such failures you must measure!

If your transmitter output is mA, put a Fluke in the loop, measure the current and read the PIW.
If it is V, measure the voltage and read the PIW.

Tell us your findings, and as said before /said before/ said before; show the wiring.

Kalle
 
My transmitter is a current (4-20 ma)
i have an amper meter in loop (on module terminals) and measure the current. i see that the current change betwen 4,12,20 and see the piw (-32767),(6941),(13883)
 
Last edited:
Yes that was indeed strange.
Could you try to exchange the code brick on the side of the card?

And please tell which terminal pins are connected?

Kalle

Edit: If my memory is correct a normal mA input should have a resistance of ca 30 ohm.
You could disconnect the card and measure both the actual channels befor and after you have exchanged the code brick.

Edit2: Try to connect -mA to M-ANA and watch the PIW.
 
Last edited:
specialy look at the grounding, not used channels set to d position and make connections to the ground
also in the first link in chapter 5.3
S7-300_400_Analog_M-Verbindungen_T1_01_e.gif
 
Last edited:

Similar Topics

hello... i'm trying to take an analog value from transmitter.. i'm using OMRON CS1G-CPU45, and the analog module is CS1W-AD16, the analog value is...
Replies
1
Views
1,443
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
15
Views
225
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
173
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
78
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
56
Back
Top Bottom