MLX 1400 Serial Issue

sethen320

Member
Join Date
Nov 2006
Location
Texas
Posts
21
This one is just weird.

I have a device which has been working great. I have done comms tests repeatedly with different PCs emulating serial strings coming from a Micrologix 1400. I finally connected my device to channel 0 using a custom cable (pins 2, 4, and 7) and my device died. While troubleshooting I realized that I forgot to switch the channel configuration from DF1 to ASCII, but I don't think that would have killed it.

Upon reading the manual further I saw some info about not connecting to certain pins due to voltage issues, but I didn't see anything regarding the mistake I had made. It could be some other factor (ESD, etc), but I'm trying to rule out any mistakes I made before I go through the trouble to build a new unit and connect it again.

Thanks,
-J
 
The only two thoughts I have without knowing more about the device you are connecting to is:

Verify your pinout. If you completely reverse the pinout then pins 4 and 7 will be correct, but pin 2 would be connected to pin 1 which has 24V

Check the minimum resistance of your device. Does it have any type of isolators on the communications channel?
 
On the Channel 0 serial port (round Mini-DIN8) of the MicroLogix 1100 and MicroLogix 1400 controllers, Pins 1 and 8 are the Data A and Data B RS-485 connection.

On the Channel 0 serial port of the MicroLogix 1000, 1200, and 1500 controllers, Pins 1 and 8 are the 24V DC auxiliary device power supply.

If your serial device could be damaged by connection to an RS-485 port, then it's possible you mis-wired the cable. If not, then it's probably a coincidence or an ESD/ground issue.
 
On the Channel 0 serial port (round Mini-DIN8) of the MicroLogix 1100 and MicroLogix 1400 controllers, Pins 1 and 8 are the Data A and Data B RS-485 connection.

On the Channel 0 serial port of the MicroLogix 1000, 1200, and 1500 controllers, Pins 1 and 8 are the 24V DC auxiliary device power supply.

Thanks for the correction Ken. I'm so used to that pesky 24V being there...
 

Similar Topics

Hey Guys, I am struggling to read data from a "JUMO" make controller using modbus RTU with MLX1400. The communication between the devices has...
Replies
18
Views
5,078
HELLO BOYS, I HAVE AN INTERROGANT, HOW CAN I MIGRATE A PROGRAM FROM A PLC MICROLOGIX 1500 TO A PLC 1400:beerchug:
Replies
1
Views
1,629
Newbie question here, I have been trying to setup a Ethernet/IP network consisting of 3 AB Micrologix 1400 plc's, one Idec HG4G-CJT22MF-B OI, and...
Replies
9
Views
3,329
I was talking to a customer on the phone. Sick kids so I couldn't get on site for a face to face. He wants me to quote against a guy that is...
Replies
23
Views
13,783
I want to know the pin configuration to communicate AB MLX1400 with labview through channel 2 (9 pin connector) in modbus RTU slave mode. Also...
Replies
3
Views
3,221
Back
Top Bottom