Wondering if it is OK to send a 4-20mA output from one card (1756-OF4) and use it as an 4-20 mA Input in to an 1756-IF8 analog input card on the same rack. This is a Controllogix and only doing it for testing/Simulation purposes.

Is it OK to Do so?

Thx.
 
Should be fine. To be safe, look at the isolation specifications and withstand voltages, and make sure that your "hot" signal from the output measured (volts) against the input common is within the safe margin before hooking it up. In the same rack, I doubt there could be any problem.

If neither signal is isolated then there may be problems. I am not intimate with those modules, but I suspect the input module has strong isolation.
 
Last edited:
Even if either I/O point doesn't have a high level of isolation, there shouldn't be a problem. Both the AO and AI would reference the same ground, being from the same 'box'.

Go for it.
 

Similar Topics

Hi, I have PLC-5 that has analog input module. The modules are setup as differential inputs so two wires go to 1+ and 1- terminals. I was...
Replies
8
Views
3,733
Hello, I'm working with a 1747-NI4 analog input module (for the first time) on a SLC503 processor. I noticed in the IO configuration within...
Replies
13
Views
4,763
In the literature for the card. It says scaling for the enginieering parameters can be done in the card. It shows what the raw data for 4 and...
Replies
2
Views
3,349
I am trying to setup an RTU with solar power and am trying to keep the power consumption low. This will have 3 pieces of equipment that I am...
Replies
7
Views
8,509
I need some help. I have a 1769-IF4 analog card that is hooked up to strain gages, the gages give a 4-20ma signal to the card. We had an...
Replies
9
Views
2,028
Back
Top Bottom