I'm no genie on PLC's.
I'm elektrician of craft, so I have the basics of it. anyhow.

I have bought myself a LOGO! 12/24RCE witch I wanna connekt 4 sensors of PT1000.

How is it that I wireconnekt the sensor to the PLC?
It's a 2wire cable that runs to the sensor. it regulates on 0-10V correkt?
I have some 6,6kohm resistors, but nomatter how I try to connekt the stuff together, it dosent seems to work when i go in "online test" with the LOGO. it either say 1000 or 0 in the "internal value"


Sooo.
How do I figure this out, anyone?
Thanks in adv.
Kim.
 
what do you mean by pt1000? is it RTD PT100 sensors ? if yes, you need an RTD input card like a LOGO AM2 PT100

The built in analog input are rated o-10v and to use it with an RTD probe, you would need an RTD transmitter converting the ohms signal to 0-10v signal.

I'm not familiar with logo programming but first we need to figure out what is the sensor signal range...
 
I thourt that the PT1000 sensors could go directly in on the PLC.
Yes. the input on the PLC is rated 0-10V.

I cant use a PT1000 sensor on the LOGO AM2 PT100 module?, correkt? it can only handle PT100'rds?

So inorder to make this setup to work, I would need what?
Currently i have
4*PT1000 sensors
1*LOGO! 12/24RCE
1*LOGO! DM8 12/24R

Since I'm using the setup for a solarheating array, i would like to use the 1000'rds due to the higer resolution.
 
PT's are platinum resistance sensors. They do not generate a voltage. Their resistance changes with temperature. Typically the analog circuit generates a constant current and reads the voltage generated by IR drop across the resistance.

The sensor output must match the PLC input.

There are devices called temperature transmitters that convert from resistance to current/voltage, but they're not cheap.
 
Correkt. a transmitter is needed

You'r correkt.
A transmitter trat converts the Ohm around to 0-10 voltage.
I thourt that it automatic would do that if you applied a +24VDC voltage to the one side of the sensor, and the other end into the input.

No can do. I e-mailed a buddy of mine that works around the world atm, and he confirmed my worst fear. I need to spend more money on the projekt, becos you'r right again - they aint cheap!

Thanks for the advices.

I'll go with the AM2 PT100/PT1000 module
 
Yesa converter is needed, if low price then look for a XTR102 (you can make yourself (the output is 4/20 mA but with one simple resistor is possible to go to 10 volts.
(have a 2 outputrelais switch between your channels.
 
You'r correkt.
A transmitter trat converts the Ohm around to 0-10 voltage.
I thourt that it automatic would do that if you applied a +24VDC voltage to the one side of the sensor, and the other end into the input.

No can do. I e-mailed a buddy of mine that works around the world atm, and he confirmed my worst fear. I need to spend more money on the projekt, becos you'r right again - they aint cheap!

Thanks for the advices.

I'll go with the AM2 PT100/PT1000 module

RTD resistance change is so small and not completly linear so you can't do it this way. This would work for a potentiometer but not for an rtd probe...

so the right logo card is the best option as you would need just a 4 input card instead of 4 individual transmitters....

I'M just surprised that the person where you bough the logo and stuff didn't helped you to buy the right card for your RTD...
 
NoFirst of all. It is posible to make it work without any aditional modules. Siemens logo počni version OBA 06, have four analog input that respond in scale 0-10V, but we have 24V (DC ofcourse) and we need to scale it down to 2V. It's simple mate. Secondly we need to close sercuit by conecting one end of pt1000 to 0V And second end to 308ohm resistor, then from second end of resistor to 2V and from 2V to analog input. That is conecting part . Then it's time for PROGRAM. My english is not to good, but point is that is posible to connect pt1000.
 
I'M just surprised that the person where you bough the logo and stuff didn't helped you to buy the right card for your RTD...

you would be amazed on what one can ran on to...
i worked on a project where designer chose PT100 for RTD and PLC card with output for thermocouples, and sales person sold him a card with analog 4-20mA output... ;);)
i could write for more :unsure: but that was by far the "funniest"
 

Similar Topics

Hi Guys Is it possible to covert a PT100 signal to PT1000 ? Please don't tell me change the probe !!! NOT Possible. I am thinking a PLC to do...
Replies
8
Views
1,884
How do major PLC manufacturers (Allen Bradley, GE, Siemens, etc.) get the temperature sensing signal for a PT100 or PT1000 into a PLC? Is there...
Replies
6
Views
6,156
I have, what might be a stupid question. I have an RTD sensor that outputs PT100 temperature, but my analyzer accepts only PT1000 signals. Is it...
Replies
14
Views
14,504
I use a 2 wire pt 1000 for tempreture sensore .but my plc analog input has 3 terminal( disign for 3 wire pt1000). How can i connect my plc to 2...
Replies
17
Views
5,191
dear friends, i have a station 300 which connected to an analog module sm331 rtd, i want to use this module to read temprature of some rooms...
Replies
1
Views
1,885
Back
Top Bottom