Hey guys, wondering if someone can help me out.

Running AB powerflex 4M drives, using 2 wire control with preset speed settings. (FWD / REV / FWD high speed)

I have the speeds set, and everything wired up, and my FWD and REV works fine, but my high speed (contact block pin #5 Digital In 1) does not engage the drive (+24v on the contact). I'm pretty sure I am missing a setting somewhere to tell the drive to acknowledge the other input, but I can't seem to find it.
 
Set parameter P108 to '4 Preset Freq'. Then the signal at terminal 5 controls the speed only. You still must use the FWD and REV to actually start motion.

Another tactic is to set terminal 5 as Jog (Option 2). It will then start and stop the drive using the frequency and acceleration set in A404 and A405 respectively.
 
Got it. thats what I was forgetting. Hell, that makes the highspeed shift easier to add to the program. Thanks!

Adding the run input to the plc rung with the highspeed did it!
 

Similar Topics

Hey I'm setting up a powerflex 755T, but in the connected components wizard during startup, I'm getting an issue where next to the start button it...
Replies
1
Views
218
Hello all, new here. I have 16 Powerflex 40’s that I am converting from DeviceNET to Ethernet. I changed all of the Comm modules to 22-COMM-E and...
Replies
3
Views
1,106
PLC L30ER V30.01 VFD PF 525 V7.0001 Running into an issue that I've never seen before. Ive configured many PF525's before so i know the...
Replies
5
Views
1,125
Hi, I have installed a number of Armor powerflex drives. They are controlled from an L81ES controllogix. DLR is on a ENT2R. I keep getting the...
Replies
5
Views
1,781
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
Replies
9
Views
2,407
Back
Top Bottom