Modbus RTU from control logix system

srv

Member
Join Date
Aug 2010
Location
QATAR
Posts
109
We have a control logix system in an existing old plant.Now we need to connect a RTU to this system to transmit some datas from the PLC.I think modbus is the only way to connect RTU to control logix plc.Do we need to add any PLC code in the plc to establish modbus communication between PLC and RTU.which port we can use for communication.ethernet or Serial port ?
 
99% if the time I do NOT use the serial port on the PLC. You can use the native serial port on some units. I would add a Prosoft card to the chassis.
 