It all depends on how you set it up. Is interrupting the light curtain part of the normal operation?
Be careful on pneumatic and fluid power presses the regulating bodies are changing some standards.
Good thing it is in the design stage. Are you using redundant fail safe valves?
ANSI B11.2 The new revision is Hydraulic and Pneumatic power presses. If you look at the OSHA listing they refer to the 1995 version of ANSI. You will be shocked at how many equipment builders are just doing single channel pneumatic circuits. They use redundant electrical power but not on the motion side.
There was a single valve failure that trapped a guys hand.
Yes, if it is not an EStop condition.
Most of the major brand safety relays could be configured(wired up) as Auto Reset.
The site/equipment Risk Assessment Safety Survey would determine if the safety curtain is or it is not an EStop circuit component.
If the light curtain is an EStop device, then the reset will have to be performed via hard wired push button.
My 2c....
A light curtain is just a switch that says something has broken it's barrier.
It is incumbent upon the machine designer/manufacturer to decide if that "switch" should be considered as a protective device (e-stop), or as a permissive device.
And it's not simple - it could be both, at different parts of the machine cycle.
Most times i've seen light curtains in a system they are "protective" (i.e. e-stop), and muting is used when it is "safe" to break the curtain. After the muting is released, the "protective" response is re-established.
And sometimes a curtain instigates a "safe response" in the area guarded, in which case it is not considered a true "safety device" at all.
Too many variables to give sound judgement on, but in my opinion a curtain should always be manually reset - it's an extra layer of confidence that the operator is not the wrong side of the curtain.