wht are the main changes has to be noticed in software and hardware
and io addressing aswell
actually i have a program in plc 5 and i am converting in control logix 5000 but i am getting some errrors with timers block transfer read and write,and using move instruction ,and most important things which i have to notice when i m converting it in to control logix 5000.
thnks for ur help
 
As far as timers, the time base in ControlLogix is always 1 millisecond. Adjust your timers accordingly. As the accumulator is a DINT (32 bits) that s quite a time range available.
 
biggest differences:

Block Transfers will have to be reworked into MSG (Message) commands ...

big tip: if your PLC-5 system used ANALOG modules, (etc.) then carefully save the "configuration" data values that were previously transferred by the Block Transfer Writes ... you'll have to MANUALLY enter those values into the new data arrays ... be sure that these arrays are created as INT locations – not the default DINTs ...

also be extremely careful with the addresses of I/O bits ... the PLC-5 uses OCTAL addresses – ControlLogix uses DECIMAL addresses ... the addresses of I/O bits past "07" will usually be renumbered ...

 

Similar Topics

HI EVERYBODY i have converted plc 5 program to contol logix 5000 .previous inn graphics we where using plc 5 with 3 wincc slaves. i have upgraded...
Replies
1
Views
2,944
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
Replies
3
Views
183
Hi guys, I have no experience when working with AllenBradley PLC, but I hope someone could clarify the result of multiplication shown in the...
Replies
14
Views
2,178
Does anyone know where I might be able to download or obtain a copy of Allen Bradley 6200-2CV5 software to convert a PLC2/30 to PLC 5? I'd like to...
Replies
6
Views
1,493
Long time viewer, first time poster. First I want to start, yes I know, PLC-2 and PLC-5 do not belong in manufacturing plants anymore, but...
Replies
5
Views
2,072
Back
Top Bottom