Hi Group, I ran into a strange one last week that had me pulling my hair out, I even called Ron for his help...
The power feeding the kiln lights at our plant in Nashville comes from a 480 delta to 208/120 wye,4 wire transformer. In checking things out, I found 116 volts from neutral to ground...so I pulled the breakers out of the panel, and found 116 volts still on the neutral, and on the CB's that were now hanging out in space. I checked the neutral bar, and noticed that it was not bonded to ground, so I pulled the power feed to the transformer ,and I still had 116 volts from the neutral to ground. I then started to remove a few wires from the neutral bar so that I could connect the bonding link...the first wire I pulled off arced as it came out, and when I checked the bar to ground it was 0 volts...what had been done was that someone had run some 480v wires up to a new set of 277volt lights way up near the top of the silo area, and had just hooked up the return to the nearest place they could find, which was this ungrounded neutral bar. After bonding the bar, everything returned to normal.
Someone's stupidity could have killed someone. There was enough current flowing thru that line that I found 4 places where the neutral wires had been melted out in the kiln.
Thanks for the help Ron.
I know that there are certain times that code stipulates that you cann't bond a neutral to ground, as in a residential subpanel, but please, make sure to bond the neutral on these transformer setups if code will allow it. The life you save might be your own.
David beerchug